Dear Expert.
I’m using factory studio 9.2
I knew that factory studio can work with S71200/1500 300/400 PLC which program in Tia portal.
But 300/400 PLC in PCS7 system, I don’t know whether factory studio con be work well. Because I heard that PCS 7 is very difficult to integrate with 3rd party scada software
Thank much
Hi Thanos,
Since the connection happens directly to the PLC, the engineering environment used (TIA Portal or PCS 7) should not matter. In this setup, FactoryStudio communicates directly with the S7-300/400 CPU using its native protocol, without going through PCS 7 engineering tools or WinCC.
That being said, we do not have access to PCS 7 to test this compatibility.
This means you’ll need to configure your device connection based on the actual addresses, offsets, and data types used in the PLC program.
1 Like